chas49 wrote:jfgw wrote:That would be the obvious reason except that,
chas49 wrote:The light only switches ON if the landing light is switched OFF.
.......
Is the landing light on a two-way switched circuit (or three-way, four-way, etc.) or is there just a single switch that controls it?
What sorts of lights are they? CFL? LED? GLS?
Julian F. G. W.
They're LEDs. The landing light is a two way switched circuit (dimmer upstairs, ordinary switch downstairs).
I haven't yet checked if it's the On/Off state of the landing light that affects the loft light, or the position of the upstairs switch.
I may be back with more details...
My theory:
3core+earth (3+E) has been used from the ground floor landing light switch to the upstairs landing light switch. (normal)
They've then used 3+E from the upstairs landing light switch to the ceiling rose.
Strictly speaking you only need 2core+earth between the ceiling rose and the upstairs switch, but, they threw in 3+E anyway (at first fix, probably threw one single 3+E cable from downstairs, hung a loop out of the upstairs switch box and then all the way to the landing ceiling rose)
The two switches should be wired L1 to L1, L2 to L2 and C to C (3 cores required+ earth)
The connection from the upstairs switch (live and switched live) should go L1 and L2 on the upstairs switch.
The 3rd core in the cable from the upstairs switch to the ceiling rose should not be connected.
(See
http://wiki.diyfaq.org.uk/index.php/2_Way_Switching first diagram under "Standard two way switching circuit" and picture a third wire connected to the common terminals going to the landling light ceiling rose)
I reckon the muppet who did the second fix (=wired it up) has made two mistakes:
1) At the upstairs switch they've connected the redundant third wire to the common connection on the switch.
2) At the ceiling rose, they have a redundant wire hanging in space, which they decided to connect to the live side of the loft light switch.
This means that the loft light switch is only energised for 3 of the 4 possible combinations of upstairs+downstairs landing lights.
To verify this:
1) Turn on the loft light, and fiddle with the landing light switches to get the loft light to come on.
2) Go through the four permutations of the landing light switches (order is unimportant, re arrange to suit)
a) Upstairs: Up, Downstairs Up
b) Upstairs: Up, Downstairs Down
c) Upstairs: Down, Downstairs Down
d) Upstairs: Down, Downstairs Up
(While you are at it, verify that two of the combinations give you "landing light" on, to ensure the absence of other muppetry)
If you find that the loft light stays on for all but one of the combinations, then the next thing to look at is where the loft light switch live feed originates, looking out for random single choc-block connections in the landing light ceiling rose.
Note that "loop in" ceiling roses have 4 sets of terminals:
3way #1: Permanent live: Live from CU/previous rose, live to next rose, live to switch.
3way #2: Neutral: from CU/previous rose, to next rose, to the bulb
3way #3: Earth
2 way: Switched earth: from the switch, to the bulb
If an examination of the landing ceiling rose reveals muppetry in the form of a extra choc-block (a "5th terminal"), (a) move the feed to the loft switch from the choc-block to the permanent live feed on the rose. and (b) ensure the remaining wire+chocblock is taped up.
If you want to complete the job, go down to the upstairs landing light, identify the 3+E which goes up to the ceiling rose, rather than downstairs to the hallway, remove and insulate the wire which goes to the Common terminal on the switch for the landing light.
PochiSoldi