Electrical query - can anyone explain?
The set-up in my free-standing garage is that power comes from the house through an armoured cable and into a fused switched spur.
Two cables lead out of the spur, one to 13A sockets and one to a lighting circuit.
The switch and the fuse only operate in relation to the lighting circuit.
This was all installed by the house builder some 40 years ago.
Today I decided to install a new light switch into the lighting circuit. Switched off at the spur, no lights. For additional safety I then removed the fuse.
Cut the wire where I wanted to install a junction box and the whole circuit tripped at the distribution board. The circuit includes part of the lounge and kitchen in the house as well as the garage.
Reset the MCB and no further issues.
I am now completely bewildered as to why cutting a 'dead' wire should/could trip the circuit.
Any thoughts?
Two cables lead out of the spur, one to 13A sockets and one to a lighting circuit.
The switch and the fuse only operate in relation to the lighting circuit.
This was all installed by the house builder some 40 years ago.
Today I decided to install a new light switch into the lighting circuit. Switched off at the spur, no lights. For additional safety I then removed the fuse.
Cut the wire where I wanted to install a junction box and the whole circuit tripped at the distribution board. The circuit includes part of the lounge and kitchen in the house as well as the garage.
Reset the MCB and no further issues.
I am now completely bewildered as to why cutting a 'dead' wire should/could trip the circuit.
Any thoughts?
-
- Lemon Quarter
- Posts: 2513
- Joined: November 18th, 2021, 11:57 am
- Has thanked: 2040 times
- Been thanked: 1228 times
Re: Electrical query - can anyone explain?
Lighting circuits in our house have to be switched off with two of the MCB's at the distribution unit, or they are still live. I have no idea if that's normal. But it's how ours is. The distribution unit was fitted new 3 years ago in a 28 year old house.
-
- Lemon Quarter
- Posts: 3904
- Joined: November 6th, 2016, 10:25 pm
- Has thanked: 1238 times
- Been thanked: 2051 times
Re: Electrical query - can anyone explain?
The switch and fuse isolate the live.
At a guess the trip is because your cutters have connected neutral to Earth, the the one that trip was a Residual Current Device rather than a plain MCB.
Paul
At a guess the trip is because your cutters have connected neutral to Earth, the the one that trip was a Residual Current Device rather than a plain MCB.
Paul
-
- Lemon Quarter
- Posts: 1348
- Joined: March 27th, 2017, 11:41 am
- Has thanked: 605 times
- Been thanked: 589 times
Re: Electrical query - can anyone explain?
My guess is this, when you turned off power at the spur there was still some kind of capacitive load on the line which meant the live wire was sitting at say 5v or so.
When you cut the cable, that 5v made contact with the earth cable, the power draining out was enough to trigger an earth leakage detection and trip the circuit breaker.
When you cut the cable, that 5v made contact with the earth cable, the power draining out was enough to trigger an earth leakage detection and trip the circuit breaker.
-
- Lemon Half
- Posts: 9107
- Joined: November 4th, 2016, 1:16 pm
- Has thanked: 4140 times
- Been thanked: 10035 times
Re: Electrical query - can anyone explain?
DrFfybes wrote:
The switch and fuse isolate the live.
At a guess the trip is because your cutters have connected neutral to Earth, [and] the one that tripped was a Residual Current Device rather than a plain MCB
I agree that this is the most likely explanation.
Cheers,
Itsallaguess
-
- Lemon Slice
- Posts: 493
- Joined: May 11th, 2017, 8:33 pm
- Has thanked: 99 times
- Been thanked: 212 times
Re: Electrical query - can anyone explain?
Thanks for all the responses. One less thing to puzzle about. Now, does anyone know the meaning of life?
-
- Lemon Slice
- Posts: 690
- Joined: February 23rd, 2023, 7:42 am
- Has thanked: 188 times
- Been thanked: 329 times
Re: Electrical query - can anyone explain?
Probably a good opportunity while you're making changes to run the live into a little consumer unit?
£40 from Screwfix complete with 2 x mcb's and a spare way for future use.
£40 from Screwfix complete with 2 x mcb's and a spare way for future use.
-
- Lemon Quarter
- Posts: 3904
- Joined: November 6th, 2016, 10:25 pm
- Has thanked: 1238 times
- Been thanked: 2051 times
Re: Electrical query - can anyone explain?
Dicky99 wrote:Probably a good opportunity while you're making changes to run the live into a little consumer unit?
£40 from Screwfix complete with 2 x mcb's and a spare way for future use.
Could be - that way if you do have a switched and fused spur you don't test the switch and find it isolates the lights, then remove the 13A fuse and assume this protects the sockets and attack the socket cable with the wire cutters. Those ones with the red and yellow handles are great, apart from a slight flash burn here the jaws exploded I was fine.
Paul
-
- Lemon Quarter
- Posts: 1348
- Joined: March 27th, 2017, 11:41 am
- Has thanked: 605 times
- Been thanked: 589 times
Re: Electrical query - can anyone explain?
DrFfybes wrote:The switch and fuse isolate the live.
At a guess the trip is because your cutters have connected neutral to Earth, the the one that trip was a Residual Current Device rather than a plain MCB.
Paul
I hadn't thought about neutral, for it to be tripping in this situation I would think about checking how good the connection is. Normal voltage difference between neutral and ground is < 2v which I wouldn't expect to be enough to trip an RCD.
-
- Lemon Half
- Posts: 5944
- Joined: November 4th, 2016, 11:22 am
- Has thanked: 4305 times
- Been thanked: 2664 times
Re: Electrical query - can anyone explain?
Lanark wrote:DrFfybes wrote:The switch and fuse isolate the live.
At a guess the trip is because your cutters have connected neutral to Earth, the the one that trip was a Residual Current Device rather than a plain MCB.
I hadn't thought about neutral, for it to be tripping in this situation I would think about checking how good the connection is. Normal voltage difference between neutral and ground is < 2v which I wouldn't expect to be enough to trip an RCD.
When I'm working on a supposedly dead circuit with these RCBO/RDC thingummys, I try to avoid connecting anything to anything, live, neutral, earth.
Was wiring some wall lights last week, had 67V of 'phantom voltage' but managed to connect them OK.
Better when we had porcelain fuse holders in a hardwood case, fuse wire you could 'upgrade' if it kept blowing for no apparent reason. Those were the days.
V8
-
- Lemon Quarter
- Posts: 3280
- Joined: December 7th, 2016, 9:09 pm
- Has thanked: 373 times
- Been thanked: 1088 times
Re: Electrical query - can anyone explain?
Lanark wrote: Normal voltage difference between neutral and ground is < 2v which I wouldn't expect to be enough to trip an RCD.
Err... I assume v stands for volts and RCD stands for Residual Current Device/disconnect?
Do I have to point out that voltage does not require a flow of current, while the point of a RCD is to disconnect when a current flow exceeds a given amount.
Dare I point out that wires are usually low resistance and that 2v though a 1 ohme resistor is 2 amps!
I would bloody hope it trips at that!
While 2v won't produce that current flow through a person, 2 amps through a person will kill.
Oh, there is a old adage that it's volts not amps that kill. That's because you need a lot of volts to push any serious amps through a human body, which has quite a high resistance. Nothing to do with RCD's.
Last edited by Urbandreamer on June 17th, 2023, 8:56 pm, edited 1 time in total.
-
- Lemon Quarter
- Posts: 3166
- Joined: November 4th, 2016, 11:12 am
- Has thanked: 3724 times
- Been thanked: 1538 times
Re: Electrical query - can anyone explain?
88V8 wrote:
Better when we had porcelain fuse holders in a hardwood case, fuse wire you could 'upgrade' if it kept blowing for no apparent reason. Those were the days.
V8
Quite, and wooden 2 pin round pin plugs. And those useful adaptors that enabled an appliance to be plugged into a light socket, like an iron. I remember my father attempting to fix a blown plug fuse by drilling a small hole in the cap at either end and trying to solder a new length of fuse wire into the fuse. Unfortunately my father couldn't solder to save his life
RC
-
- Lemon Half
- Posts: 7358
- Joined: November 24th, 2016, 3:29 am
- Has thanked: 1709 times
- Been thanked: 3934 times
Re: Electrical query - can anyone explain?
Urbandreamer wrote:Lanark wrote: Normal voltage difference between neutral and ground is < 2v which I wouldn't expect to be enough to trip an RCD.
Err... I assume v stands for volts and RCD stands for Residual Current Device/disconnect?
Do I have to point out that voltage does not require a flow of current, while the point of a RCD is to disconnect when a current flow exceeds a given amount.
Dare I point out that wires are usually low resistance and that 2v though a 1 ohme resistor is 2 amps!
I would bloody hope it trips at that!
While 2v won't produce that current flow through a person, 2 amps through a person will kill.
Oh, there is a old adage that it's volts not amps that kill. That's because you need a lot of volts to push any serious amps through a human body, which has quite a high resistance. Nothing to do with RCD's.
Not only all that but there the obvious puzzle remains. How does ANY current flow when the circuit is isolated by a switched fused spur (FCU in today's parlance) which is a double pole switch, i.e. one which disconnects both live and neutral conductors?
I reckon the FCU must be faulty and only disconnecting one conductor.
-
- Lemon Quarter
- Posts: 1051
- Joined: November 5th, 2016, 12:26 pm
- Has thanked: 226 times
- Been thanked: 207 times
Re: Electrical query - can anyone explain?
Urbandreamer wrote:Oh, there is an old adage that it's volts not amps that kill. That's because you need a lot of volts to push any serious amps through a human body, which has quite a high resistance. Nothing to do with RCD's.
The old adage I used to tell my guys is “it’s volts that jolts but it’s mills that kills”. There’s a reason for the common 30mA breaker limit. How many volts it takes to achieve that is dependent on conditions at the time (eg how sweaty your hands might be) but even the standard industrial 110V centre-tapped to earth isn’t guaranteed safe.
-
- Lemon Quarter
- Posts: 2593
- Joined: November 4th, 2016, 3:36 pm
- Has thanked: 1120 times
- Been thanked: 1181 times
Re: Electrical query - can anyone explain?
BullDog wrote:Lighting circuits in our house have to be switched off with two of the MCB's at the distribution unit, or they are still live. I have no idea if that's normal. But it's how ours is. The distribution unit was fitted new 3 years ago in a 28 year old house.
That is definitely not normal!!! It is not as dangerous as it might seem (for a lighting circuit) but I, personally, would want to rectify the fault ASAP.
Regarding the OP, I agree with the comments regarding an rcd (or rcbo) tripping. If it was an mcb, post back! (an mcb does not have a test button.)
Mike4 wrote:Not only all that but there the obvious puzzle remains. How does ANY current flow when the circuit is isolated by a switched fused spur (FCU in today's parlance) which is a double pole switch, i.e. one which disconnects both live and neutral conductors?
I understand that single-pole FCUs exist, not that either of us would buy such low quality products.
Julian F. G. W.
-
- Lemon Half
- Posts: 5944
- Joined: November 4th, 2016, 11:22 am
- Has thanked: 4305 times
- Been thanked: 2664 times
Re: Electrical query - can anyone explain?
BullDog wrote:Lighting circuits in our house have to be switched off with two of the MCB's at the distribution unit, or they are still live. I have no idea if that's normal. But it's how ours is. The distribution unit was fitted new 3 years ago in a 28 year old house.
I wonder if there is a two-way switch with a borrowed neutral.
V8
-
- Lemon Quarter
- Posts: 2513
- Joined: November 18th, 2021, 11:57 am
- Has thanked: 2040 times
- Been thanked: 1228 times
Re: Electrical query - can anyone explain?
88V8 wrote:BullDog wrote:Lighting circuits in our house have to be switched off with two of the MCB's at the distribution unit, or they are still live. I have no idea if that's normal. But it's how ours is. The distribution unit was fitted new 3 years ago in a 28 year old house.
I wonder if there is a two-way switch with a borrowed neutral.
V8
There's several of them upstairs and downstairs lighting circuits. Definitely have to switch two MCBs off to make the lights go out. That's how I know this. I changed a few light switches myself and actuated the MCBs until I knew I'd selected the correct lighting circuits.
I'm definitely not an electrician (a retired CEng) so I'm super cautious with electric electrickery. The consumer unit was replaced 3 years ago by a local electrician we have known for years and he issued a testing certificate to us to keep. I don't really think we have a problem.
-
- Lemon Half
- Posts: 9107
- Joined: November 4th, 2016, 1:16 pm
- Has thanked: 4140 times
- Been thanked: 10035 times
Re: Electrical query - can anyone explain?
BullDog wrote:88V8 wrote:
I wonder if there is a two-way switch with a borrowed neutral.
There's several of them upstairs and downstairs lighting circuits. Definitely have to switch two MCBs off to make the lights go out. That's how I know this. I changed a few light switches myself and actuated the MCBs until I knew I'd selected the correct lighting circuits.
I'm definitely not an electrician (a retired CEng) so I'm super cautious with electric electrickery. The consumer unit was replaced 3 years ago by a local electrician we have known for years and he issued a testing certificate to us to keep. I don't really think we have a problem.
Having separate lighting circuits for each floor of the house is a common situation, but I suspect that the way you've introduced that concept in the linked post below might have been mis-understood to read that any particular light in your house can only be electrically isolated when TWO different MCB's are turned off at the same time, which of course would be a dangerous and incorrectly wired situation -
https://www.lemonfool.co.uk/viewtopic.php?f=40&t=39534#p595957
When I read your earlier post, I understood you to be simply talking about two separate electrical circuits, so it might be worth helping to clear up the above linked confusion if that is what you meant?
Cheers,
Itsallaguess
-
- Lemon Quarter
- Posts: 2513
- Joined: November 18th, 2021, 11:57 am
- Has thanked: 2040 times
- Been thanked: 1228 times
Re: Electrical query - can anyone explain?
Itsallaguess wrote:Having separate lighting circuits for each floor of the house is a common situation, but I suspect that the way you've introduced that concept in the linked post below might have been mis-understood to read that any particular light in your house can only be electrically isolated when TWO different MCB's are turned off at the same time, which of course would be a dangerous and incorrectly wired situation -
https://www.lemonfool.co.uk/viewtopic.php?f=40&t=39534#p595957
When I read your earlier post, I understood you to be simply talking about two separate electrical circuits, so it might be worth helping to clear up the above linked confusion if that is what you meant?
Cheers,
Itsallaguess
Thanks. For example, for the downstairs lights to go out, I need to switch two MCBs. They are both marked lighting circuit by the electrician who installed the consumer unit.
-
- Lemon Half
- Posts: 7358
- Joined: November 24th, 2016, 3:29 am
- Has thanked: 1709 times
- Been thanked: 3934 times
Re: Electrical query - can anyone explain?
BullDog wrote:Itsallaguess wrote:Having separate lighting circuits for each floor of the house is a common situation, but I suspect that the way you've introduced that concept in the linked post below might have been mis-understood to read that any particular light in your house can only be electrically isolated when TWO different MCB's are turned off at the same time, which of course would be a dangerous and incorrectly wired situation -
https://www.lemonfool.co.uk/viewtopic.php?f=40&t=39534#p595957
When I read your earlier post, I understood you to be simply talking about two separate electrical circuits, so it might be worth helping to clear up the above linked confusion if that is what you meant?
Cheers,
Itsallaguess
Thanks. For example, for the downstairs lights to go out, I need to switch two MCBs. They are both marked lighting circuit by the electrician who installed the consumer unit.
This sounds very wrong to me. So to turn off any one single downstairs light, any light, you have to turn off two MCBs at the same time? Or do you mean to extinguish ALL of the downstairs lights (as opposed to just some of them), two MCBs must be turned off?
Assuming the former, having turned off these two MCBs, turning either of them back on will make the light come back ON again?
If so, then you must have two MCBs in parallel. Either a wiring error, or a monumental bodge to stop tripping when lots of lights are on at the same time, I'd have thought.