Donate to Remove ads

Got a credit card? use our Credit Card & Finance Calculators

Thanks to Wasron,jfgw,Rhyd6,eyeball08,Wondergirly, for Donating to support the site

Replacing fluorescent tube with LED

Does what it says on the tin
MyNameIsUrl
Lemon Slice
Posts: 479
Joined: November 4th, 2016, 1:56 pm
Has thanked: 1308 times
Been thanked: 108 times

Replacing fluorescent tube with LED

#620377

Postby MyNameIsUrl » October 13th, 2023, 12:22 pm

I can’t get the new LED tube to work. I’ve replaced the starter with a ‘LED fuse’. I’ve opened up the fitting to check if that’s faulty but as far as I can tell there is voltage where I would expect it to be, although I don’t understand the need for 4 terminals.

Now I’ve just noticed the new LED tube has L and N marked at one end, so I’ve tried it in every orientation but still not working. Do I need to rewire the fitting? Have I bought the wrong tube?

Laughton
Lemon Slice
Posts: 909
Joined: November 6th, 2016, 2:15 pm
Has thanked: 142 times
Been thanked: 335 times

Re: Replacing fluorescent tube with LED

#620384

Postby Laughton » October 13th, 2023, 12:53 pm

Bear in mind that I'm not an electrician but when you say a new LED tube, do you mean you've bought an LED tube that is designed to fit into your existing fluoresent light fitting?

I fairly recently replaced all (12) fluoresent lights in our garage and lofts with all in one LED light fittings (I think they're called battens). They look nicer, give off much more light, fitting was super simple and hopefully much cheaper to run.

The ones I used are no longer available but similar, I think, to these (other makes and models are available): -

https://www.screwfix.com/p/lap-single-5 ... 240v/667pp

MyNameIsUrl
Lemon Slice
Posts: 479
Joined: November 4th, 2016, 1:56 pm
Has thanked: 1308 times
Been thanked: 108 times

Re: Replacing fluorescent tube with LED

#620397

Postby MyNameIsUrl » October 13th, 2023, 1:22 pm

Laughton wrote:Bear in mind that I'm not an electrician but when you say a new LED tube, do you mean you've bought an LED tube that is designed to fit into your existing fluoresent light fitting?

Yes, that's it exactly. The old fluorescent tube flickered and flashed and one end of the glass was blackened, so I wanted to replace it with a LED tube which uses less energy.

eepee
Lemon Slice
Posts: 281
Joined: April 11th, 2017, 5:27 pm
Has thanked: 50 times
Been thanked: 83 times

Re: Replacing fluorescent tube with LED

#620405

Postby eepee » October 13th, 2023, 2:00 pm

I bought a couple of these:-

https://www.lyco.co.uk/v-tac-50w-cool-w ... gLSXPD_BwE

As replacements in a kitchen.

Once fitted, I had to remove one - it was way brighter than the original two flo tubes!

Regards,
ep

Tedx
Lemon Quarter
Posts: 2075
Joined: December 14th, 2022, 10:59 am
Has thanked: 1849 times
Been thanked: 1489 times

Re: Replacing fluorescent tube with LED

#620409

Postby Tedx » October 13th, 2023, 2:56 pm

I have an LED stoplight in my loft. Flip the switch and it's like a nuclear weapon going off.

There are no dark corners in my loft anymore.

DrFfybes
Lemon Quarter
Posts: 3791
Joined: November 6th, 2016, 10:25 pm
Has thanked: 1198 times
Been thanked: 1987 times

Re: Replacing fluorescent tube with LED

#620419

Postby DrFfybes » October 13th, 2023, 3:45 pm

Laughton wrote:I fairly recently replaced all (12) fluoresent lights in our garage and lofts with all in one LED light fittings (I think they're called battens). They look nicer, give off much more light, fitting was super simple and hopefully much cheaper to run.


You might be surprised. I replaced a 6 foor Fluorescent with an LED batten and the difference was about 20%, although the LED was £20 rather than under a fiver. IIRC it was a General Electric or similar well known brand.

It lasted about a year, so I put a traditional one back in.

However they are improving, a 4 foot LED batten is 36W (they're about 9W/foot) and about 3500 lumens. A 1200mm LED batten tends to be about 18W but are circa 2000 Lm, so similar lumens/Watt. However the new slimline battens only emit light in one direction unlike a traditional tube, so the lower output often provides as good illumination.

Back to the OP...

As for whether you need to rewire, look at the ballast/driver in your existing fitting and Google the model and see what type it is (magnetic or electronic) as one type can need modifying.

csearle
Lemon Quarter
Posts: 4838
Joined: November 4th, 2016, 2:24 pm
Has thanked: 4861 times
Been thanked: 2124 times

Re: Replacing fluorescent tube with LED

#620422

Postby csearle » October 13th, 2023, 3:55 pm

MyNameIsUrl wrote:I can’t get the new LED tube to work. I’ve replaced the starter with a ‘LED fuse’. I’ve opened up the fitting to check if that’s faulty but as far as I can tell there is voltage where I would expect it to be, although I don’t understand the need for 4 terminals.

Now I’ve just noticed the new LED tube has L and N marked at one end, so I’ve tried it in every orientation but still not working. Do I need to rewire the fitting? Have I bought the wrong tube?
One I recently replaced said in the instructions that it wasn't suitable for all fluorescent light fittings. I installed it. It didn't work. I swapped ends, still didn't work. I too noticed that it had an L and N at one end. After a bit of fiddling about with a continuity tester I decided to simply connect the L and N respectively to line and neutral. New LED "tube" lit up.

So I just rewired the fitting's innards to ignore the electronic ballast inside and supply the LED "tube" instead.

Chris
PS I think the remaining two terminals are to complete the circuit so that the LED "tube" can hope to work in fittings with older ballasts.

MyNameIsUrl
Lemon Slice
Posts: 479
Joined: November 4th, 2016, 1:56 pm
Has thanked: 1308 times
Been thanked: 108 times

Re: Replacing fluorescent tube with LED

#620430

Postby MyNameIsUrl » October 13th, 2023, 4:48 pm

csearle wrote:So I just rewired the fitting's innards to ignore the electronic ballast inside and supply the LED "tube" instead.

Thanks Chris, so just to be clear you just took the live and neutral entering the enclosure and rearranged them to one 'socket' end of the fitting? Obviously preserve all the earths, but as simple as that? I guess I won't need the 'LED fuse' which replaces the starter either?

csearle
Lemon Quarter
Posts: 4838
Joined: November 4th, 2016, 2:24 pm
Has thanked: 4861 times
Been thanked: 2124 times

Re: Replacing fluorescent tube with LED

#620432

Postby csearle » October 13th, 2023, 4:57 pm

MyNameIsUrl wrote:
csearle wrote:So I just rewired the fitting's innards to ignore the electronic ballast inside and supply the LED "tube" instead.

Thanks Chris, so just to be clear you just took the live and neutral entering the enclosure and rearranged them to one 'socket' end of the fitting? Obviously preserve all the earths, but as simple as that? I guess I won't need the 'LED fuse' which replaces the starter either?
Well that is exactly what I did, yes.

My fluorescent didn't have a starter so I didn't have one to replace. Is it really a "fuse" or are the terminals just linked together (which will ultimately be a fuse at some current I realise, but you know what I mean)?

Even if it is a fuse, the lighting circuit will be on a 6A trip switch* so I wouldn't lose any sleep over it. If you are concerned then you could rewire it to supply the LED "tube" via the "dummy starter".

Chris
* Could, less commonly, also be a 10A trip switch or a 5A fuse.

quelquod
Lemon Quarter
Posts: 1041
Joined: November 5th, 2016, 12:26 pm
Has thanked: 218 times
Been thanked: 205 times

Re: Replacing fluorescent tube with LED

#620438

Postby quelquod » October 13th, 2023, 5:16 pm

Others’ experiences likely differ but my experience with LED battens is pretty poor. Out of 10 6’ battens 3 needed replacing inside a few months due to flashing periodically after they’d been on for a few hours. 3 different makes (all Chinese though I guess). Same problem with all of them which was the power supply tripping in and out probably due to overheating. All replaced under guarantee so just a nuisance rather than real cost. The power supplies concerned have no obvious way to dissipate heat with the plastic construction so maybe a bit of aluminium under them might fix them - the vendor wasn’t inclined to pay for their return postage so I’ll experiment. On the plus side when they work they are really bright partly because (as mentioned earlier) they aren’t omnidirectional.

As a by the way I’ve had problems with some of the fancy filament-style lamps too (mostly 100 watt equivalents) where one or more strands have failed dimming the light considerably. With their cost it doesn’t take long to erode the hoped-for energy cost savings!

MyNameIsUrl
Lemon Slice
Posts: 479
Joined: November 4th, 2016, 1:56 pm
Has thanked: 1308 times
Been thanked: 108 times

Re: Replacing fluorescent tube with LED

#620440

Postby MyNameIsUrl » October 13th, 2023, 5:23 pm

csearle wrote:Is it really a "fuse" or are the terminals just linked together

Out of curiosity I just opened it up - there's a tiny glass fuse marked 250mA 250V which seems enough for a 14W lamp

csearle
Lemon Quarter
Posts: 4838
Joined: November 4th, 2016, 2:24 pm
Has thanked: 4861 times
Been thanked: 2124 times

Re: Replacing fluorescent tube with LED

#620441

Postby csearle » October 13th, 2023, 5:27 pm

quelquod wrote:...due to flashing periodically after they’d been on for a few hours. 3 different makes (all Chinese though I guess).
Have you checked it isn't Morse code? These guys might try anything. C.

csearle
Lemon Quarter
Posts: 4838
Joined: November 4th, 2016, 2:24 pm
Has thanked: 4861 times
Been thanked: 2124 times

Re: Replacing fluorescent tube with LED

#620457

Postby csearle » October 13th, 2023, 6:33 pm

MyNameIsUrl wrote:
csearle wrote:Is it really a "fuse" or are the terminals just linked together

Out of curiosity I just opened it up - there's a tiny glass fuse marked 250mA 250V which seems enough for a 14W lamp
Interesting. In that case I'd wire it in if I were you. C.

jaizan
Lemon Slice
Posts: 403
Joined: September 1st, 2018, 10:21 pm
Has thanked: 228 times
Been thanked: 116 times

Re: Replacing fluorescent tube with LED

#620481

Postby jaizan » October 13th, 2023, 9:58 pm

MyNameIsUrl wrote:Now I’ve just noticed the new LED tube has L and N marked at one end

This is normal. Throw away the old fitting.
Brown/Red to L, Blue/Black to N and it should work. If there is any doubt about the light, test it by wiring it to a 3-pin plug instead.

A little care is needed with light fittings, as at the ceiling, you tend to have the ring main & a live & neutral going off to the switch. It's easy to get wrong if not paying attention.

Mike4
Lemon Half
Posts: 7207
Joined: November 24th, 2016, 3:29 am
Has thanked: 1670 times
Been thanked: 3841 times

Re: Replacing fluorescent tube with LED

#620482

Postby Mike4 » October 13th, 2023, 10:08 pm

jaizan wrote:
MyNameIsUrl wrote:Now I’ve just noticed the new LED tube has L and N marked at one end

This is normal. Throw away the old fitting.
Brown/Red to L, Blue/Black to N and it should work. If there is any doubt about the light, test it by wiring it to a 3-pin plug instead.

A little care is needed with light fittings, as at the ceiling, you tend to have the ring main & a live & neutral going off to the switch. It's easy to get wrong if not paying attention.


I can't help but suggest you re-think this bit!

csearle
Lemon Quarter
Posts: 4838
Joined: November 4th, 2016, 2:24 pm
Has thanked: 4861 times
Been thanked: 2124 times

Re: Replacing fluorescent tube with LED

#620483

Postby csearle » October 13th, 2023, 10:09 pm

jaizan wrote:A little care is needed with light fittings, as at the ceiling, you tend to have the ring main & a live & neutral going off to the switch. It's easy to get wrong if not paying attention.
At the risk of being picky, lighting circuits are never "ring mains" they are radial circuits and, when the lighting circuit from the consumer unit is present at the light fitting, the cable that goes off to the switch won't have a neutral in it, but rather a permanent live going down and a switched live coming back up, aka a switch-drop.

(But I agree with you that a little care should be taken as the switched-live coming back up from the switch is usually on the blue (or black) insulated conductor.)

C.

Mike4
Lemon Half
Posts: 7207
Joined: November 24th, 2016, 3:29 am
Has thanked: 1670 times
Been thanked: 3841 times

Re: Replacing fluorescent tube with LED

#620526

Postby Mike4 » October 14th, 2023, 10:02 am

csearle wrote:
jaizan wrote:A little care is needed with light fittings, as at the ceiling, you tend to have the ring main & a live & neutral going off to the switch. It's easy to get wrong if not paying attention.
At the risk of being picky, lighting circuits are never "ring mains" they are radial circuits and, when the lighting circuit from the consumer unit is present at the light fitting, the cable that goes off to the switch won't have a neutral in it, but rather a permanent live going down and a switched live coming back up, aka a switch-drop.

(But I agree with you that a little care should be taken as the switched-live coming back up from the switch is usually on the blue (or black) insulated conductor.)

C.


I'm always surprised that using ordinary T&E cable for the switch drop is permissible given the confusion sometimes caused by using the black or blue as a live conductor.

Special cable with say, brown and grey insulated conductors and an earth should be made for switch drops, in my opinion as a gas bod!

88V8
Lemon Half
Posts: 5843
Joined: November 4th, 2016, 11:22 am
Has thanked: 4199 times
Been thanked: 2603 times

Re: Replacing fluorescent tube with LED

#620539

Postby 88V8 » October 14th, 2023, 10:34 am

Mike4 wrote:
csearle wrote:(But I agree with you that a little care should be taken as the switched-live coming back up from the switch is usually on the blue (or black) insulated conductor.)

I'm always surprised that using ordinary T&E cable for the switch drop is permissible given the confusion sometimes caused by using the black or blue as a live conductor.
Special cable with say, brown and grey insulated conductors and an earth should be made for switch drops, in my opinion as a gas bod!

One can put red sleeving on the black, or red tape. I sometimes do, more so in j-boxes where it can get really confusing.

I remember getting well confused when wiring my previous garage, ended up with several incandescent fittings in series and couldn't understand why they were all so dim.

Regards LED battens, I have seven in my garage/workshop, since 2016, none has needed replacing. There is one surviving fluorescent that I keep in there for nostalgia, its glow-worm emissions a link to an ancient world.

V8

csearle
Lemon Quarter
Posts: 4838
Joined: November 4th, 2016, 2:24 pm
Has thanked: 4861 times
Been thanked: 2124 times

Re: Replacing fluorescent tube with LED

#620542

Postby csearle » October 14th, 2023, 10:51 am

Mike4 wrote:Special cable with say, brown and grey insulated conductors and an earth should be made for switch drops, in my opinion as a gas bod!
They do sell twin and earth with two browns in it for switch drops but this would mean hauling yet another drum of cable all around Kent and Sussex. More convenient to sleeve up the blue with a bit of brown sleeving.

If you had brown and grey then you should still sleeve up the grey as it is reserved for three-phase.

C.


Return to “Building and DIY”

Who is online

Users browsing this forum: Bing [Bot] and 35 guests